I’ve recently become the owner of a home that was constructed in the mid 1950s (in the US). As such, not all the outlets are grounded, three-prong receptacles, since that wasn’t code-required at the time. It looks like a few have been added or upgraded over the years, but there are still many that are ungrounded. What is the best way to go about converting those receptacles to be grounded? Will that require a professional? It seems like probably the kind of electrical work that I am capable of doing myself, but I am also very much not an electrician.

  • CompactFlax
    link
    fedilink
    English
    arrow-up
    7
    ·
    17 days ago

    GFCI doesn’t change the fact that there is potentially no ground wire.

    • keckbug@lemmy.world
      link
      fedilink
      arrow-up
      9
      ·
      17 days ago

      Well no, but short of a rewire, a gfci with sticker is the code-compliant way to plug in three pin plugs to an ungrounded receptacle.

      A rewire is the right solution but utterly impractical for many. Just silently swapping in new receptacles and leaving the ground unconnected is easy but not compliant. This is the middle ground.